CCS32Clara: Difference between revisions
(extended parameter descriptions regarding inlet voltage options) |
(parameter details for ppvariant) |
Line 89: | Line 89: | ||
|9 | |9 | ||
|0 | |0 | ||
|Various circuit variations exist for PP resistor measurement. "1" is correct for the latest hardware | |Various circuit variations exist for PP resistor measurement. "1" is correct for the latest hardware (Foccci 4.2 and above) Technically, ppvariant=1 is the correct setting for Foccci with the PP circuit with 330 ohm pull-up to 5V and a 3k pull-down and a 47k by 47k divider. | ||
|WakeupPinFunc | |WakeupPinFunc |
Revision as of 06:18, 14 June 2024
Disclaimer: This Page is still work in progress! Any information written here is a draft only and should be handled as such. Contributions are more than welcome. If you have questions, please ask them in the discussion section of the page or in the OpenInverter Forum.
This page is about the reference software for the Fully OpenSource CCS Charge Controller (Foccci). CCS32Clara (also referred to as "Clara") is currently under development by the OpenInverter Community.
Here you will find documentation (or reference) on how to setup Clara, News on the development, diagrams, open ToDos, etc.
Clara in the OpenInverterForum.
Configuring Clara via CAN
Clara exposes only one single CAN interface for vehicle communication and initial configuration. So we need a CAN counterpart to talk to it.
There are two main approaches to this: a) use a command line tool [1] or b) use an ESP based CAN module [2]
Both ways require knowing Claras so called Node Id (similar to an IP address on a local network). By default this is 22. You can enter this node id on the bottom left navigation bar.
Name | Unit | Min | Max | Default | Description |
Hardware Config | |||||
UdcDivider | dig/V | 0 | 100 | 10 | Division factor from ADC digits to V of external voltage measurement board.
In other words: The UdcDivider is the configuration parameter which defines the scaling of the physical inlet voltage measurement circuit. That's why it is only relevant if a physical inlet voltage measurement circuit is present, and if the parameter InletVtgSrc is 1, means the Clara will measure the inlet voltage with the analog input. CAN mapping makes no sense for the UdcDivider, because it is a fix value. It is the ratio between the voltage on the inlet and the digital value on the AD converter. |
EconomizerDuty | % | 0 | 100 | 100 | Contactor economizer duty cycle. Contactors are always turned on with 12V for 1s then drop to this value. Set to 100% if your contactor has a built-in economizer |
InletVtgSrc | 0 | 2 | 0 | Inlet Voltage Source. There are three option where Clara gets the CCS inlet voltage from:
0 - Charger output voltage (EVSEPresentVoltage) is considered equal to charge port inlet voltage 1 - Analog input U_IN_HV is used for measuring charge port inlet voltage 2 - Charge port inlet voltage is provided via CAN - don't forget to map something to InletVoltage
LockDuty | % | -100 | 100 | 30 | H-bridge duty cycle for operating the lock. Use negative value if lock polarity is swapped |
LockRunTime | ms | 0 | 10000 | 1000 | Timeout for lock operation |
LockClosedThresh | dig | 0 | 4095 | 0 | Lock feedback value for closed |
LockOpenThresh | dig | 0 | 4095 | 0 | Lock feedback value for open - if equal to lockclosethr no feedback is assumed and lock is operated timed |
ppvariant | 0 | 9 | 0 | Various circuit variations exist for PP resistor measurement. "1" is correct for the latest hardware (Foccci 4.2 and above) Technically, ppvariant=1 is the correct setting for Foccci with the PP circuit with 330 ohm pull-up to 5V and a 3k pull-down and a 47k by 47k divider. | |
WakeupPinFunc | 0 | 4 | 0 | Configure what the wakeup pin does. TODO: describe below | |
Communication | |||||
NodeId | 1 | 63 | 22 | CANOpen node id for SDO requests | |
CanSpeed | 0 | 4 | 2 | Baud rate of CAN interface 0=125k, 1=250k, 2=500k, 3=800k, 4=1M - when configuring this != 500k you will loose communication to the ESP web interface! | |
Charge Parameters | |||||
MaxPower | kW | 0 | 1000 | 100 | Absolute maximum charge power. Clara will announce this value in the ChargeParameterDiscoveryRequest message in the element EVMaximumPowerLimit. The charger may or may not respect this limitation. |
MaxVoltage | V | 0 | 1000 | 410 | Over voltage threshold. Always set about 10-20V higher then desired battery full voltage. Clara will announce this value in the ChargeParameterDiscoveryRequest message to the charger, in the element EVMaximumVoltageLimit. The charger may or may not respect this limitation. Some chargers shut down, if this limit is reached. That's why it is recommended to set it some volts higher than the voltage which is used during normal charging. |
MaxCurrent | A | 0 | 500 | 125 | Absolute maximum charge current. Clara will announce this value in the ChargeParameterDiscoveryRequest, in the element EVMaximumCurrentLimit. The charger may or may not respect this limitation. |
TargetVoltage | V | 0 | 1000 | 0 | Charge target voltage (volatile) |
ChargeCurrent | A | 0 | 500 | 0 | Instantaneous current setpoint (volatile) |
soc | % | 0 | 100 | 0 | Battery SoC for display on charger (volatile) |
BatteryVoltage | V | 0 | 1000 | 0 | Present battery voltage for precharge state (volatile) |
enable | 0 | 1 | 1 | When 0 charging is stopped/not started (volatile) | |
AcObcState | 0 | 15 | 0 | Feedback from OBC | |
Testing | |||||
DemoVoltage | V | 0 | 500 | 0 | Voltage for light bulb demo. To use the board without CAN, to get an constant voltage. Is ignored as long democtrl is not STANDALONE. Only values between 150V and 250V are accepted, others are treated as zero. |
DemoControl | 0 | 511 | 0 | Enables the standalone demo mode if value is set to STANDALONE. In this mode, no CAN is required and the target voltages for precharge and charging loop are taken from demovtg. | |
ActuatorTest | 0 | 7 | 0 | Tests various outputs | |
logging | 0 | 2047 | Selects which modules log to the serial console |
Spot values
Name | Unit | Description |
opmode | State of the CCS state machine | |
version | ||
lasterr | Last detected error | |
EvseVoltage | V | Outlet voltage reported by EVSE |
EvseCurrent | A | Outlet current reported by EVSE |
InletVoltage | V | Charge port voltage |
EvseMaxCurrent | A | Maximum current the EVSE can deliver |
EvseMaxVoltage | V | Maximum voltage the EVSE can deliver |
ControlPilotDuty | % | The PWM ratio of the CP line. This is normally 5% for DC chargers, and between 10% and 90% for analog AC chargers.
Typical values are explained here: IEC 62196 Typ 2 – Wikipedia |
temp1, 2, 3 | °C | Temperatures of the temperature sensors. Requires correct calibration values depending on the used NTC types. |
MaxTemp | °C | Maximum of the above |
ContactorDuty | % | Duty cycle of charge port contactor driver |
AdcLockFeedback | digit | Feedback value from charge port lock |
AdcProximityPilot | digit | Analog value of the PP line. This is the raw value of the analog-to-digital-converter in range 0 to 4095. |
ResistanceProximityPilot | ohm | Measured resistance between PP line and ground. Requires correct setting of the parameter ppvariant. |
CableCurrentLimit | A | Based on the PP resistance. The current limit of the charging cable for AC charging. |
EvseCurrentLimit | A | Based on the CP PWM. The current limit of the charging station for AC charging. |
AdcHwVariant | digit | raw AD value of the hardware variant coding input. Used to detect which variant of Foccci the software runs on. |
AdcIpropi | digit | raw AD value of the current sensor for the charge port lock motor driver. |
LockState | State of charge port lock | |
StopReason | ||
checkpoint | ||
CanWatchdog | 100 ms | Time since last ChargeCurrent update. When it reaches 30 (3s) the charge session is stopped |
cpuload |
Errors
Error | Description |
CANTIMEOUT | The message mapped to canwatchdog hasn't been received for over 1s or nothing is mapped to canwatchdog |
PLCTIMEOUT | PLC communication with charger timed out |
PRECTIMEOUT | Precharging the EVSE output to specified voltage timed out or battery voltage is below minimum EVSE output voltage |
LOCKTIMEOUT | The connector lock didn't reach the desired position in time |
EVSEFAULT | The EVSE reported an error and stopped |
RELAYWELDED | A welded charge port relay was detected |
Making Clara talk CHAdeMO on the CAN side
- UdcDivider - Actually, here we just select some dummy item as the important bit is in the Offset field: the version. In this case I signal non-existent CDM version 10. This tells the CDM module in my car that it talks to Clara. It then includes the battery voltage in some unused message bytes - see below.
- EvseVoltage - Transmits the charger's present output voltage back to the vehicle.
- EvseCurrent - Transmits the charger's present output current back to the vehicle.
- opmode - Observe the weird gain - this is forged to map Clara state "CurrentDemand (13)" to CDM state "ConnectorLocked (4)". In my car's CDM module this is sufficient to initiate the charging progress. You may need to change it so that the ChargeEnable flag together with ConnectorLocked is forged (numerical value 5).
- EvseMaxVoltage - Transmits the EVSE's maximum output voltage back to the vehicle.
- EvseMaxCurrent - Transmits the EVSE's maximum output current back to the vehicle.
- BatteryVoltage - Transmits the present battery voltage to the EVSE. This is the special item that normally doesn't exist in CDM and that unfortunately will prevent you from using this solution with an OEM car in a safe manner. Of course, you could manually set this to some medium battery voltage like 360V, but if you arrive with a really low battery at, say, 300V this might weld your charge port contactors. You could also manually enter the battery voltage before each charging session.
- TargetVoltage - Transmits the charge end voltage to the EVSE.
- ChargeCurrent - By far the most important data item: the charge current request.
- soc - In CDM this isn't normally a percentage value but some encoded kWh value. In my car's CDM module I specify a full battery as "200" (no idea what this actually means in kWh) and thereby can just output the SoC in 0.5% steps.
- enable - The car's charge enable flag. When 0 will stop the CCS session.
As an additional safety measure you could connect CDM pin 4 (charge enable) to Clara's button input (at least once we added an active low mode for it). It might also be worthwhile to connect pin 7 (connection check) to the PP input for drive away protection when CDM is plugged in but not charging (again, once we have actually implemented this).
- Pin 1 - GND
- Pin 2 (12V, charger start/stop) - 12V (I take it from cigarette lighter)
- Pin 4 (charging enable) - Foccci BUTTON
- Pin 5, 6 - Power pins, triple check correct polarity!
- Pin 7 (Connection check) - Foccci PP
- Pin 8, 9 (CAN) - Foccci CANL, CANH
- Pin 10 (charger start/stop 2) - Foccci SW1_LS