Added link to FOC tuning |
| (29 intermediate revisions by 9 users not shown) | |||
| Line 60: | Line 60: | ||
| colspan="6" |'''Motor (FOC)''' | | colspan="6" |'''Motor (FOC)''' | ||
| | |iqkp | ||
|0 | |0 | ||
|20000 | |20000 | ||
|64 | |64 | ||
|Current controller proportional gain | |Current controller proportional gain. Low inductance/resistance motors need less, high inductance/resistance motors more | ||
|idkp | |||
|0 | |||
|20000 | |||
|64 | |||
|Same as above but often a little higher then iqkp | |||
|curki | |curki | ||
| Line 72: | Line 79: | ||
|100000 | |100000 | ||
|20000 | |20000 | ||
|Current controller integral gain | |Current controller integral gain (id and iq) | ||
| | |exckp | ||
|0 | |0 | ||
|20000 | |||
|3000 | |||
|Exciter controller gain (Renault Zoe variant only) | |||
|cogkp | |||
| -1000 | |||
|1000 | |1000 | ||
| | |0 | ||
| | |[https://openinverter.org/forum/viewtopic.php?t=5660 Anti-cogging modulator] gain. This generates a trapezoidal wave form to counter the cogging current of IPM motors. | ||
|cogph | |||
|0 | |||
|65535 | |||
|0 | |||
|Anti-cogging modulator phase angle between cogging current and electrical rotor angle | |||
|cogmax | |||
|0 | |||
|30000 | |||
|0 | |||
|Maximum amplitude of the anti-cogging current | |||
|vlimflt | |||
| 0 | |||
|16 | |||
| 10 | |||
|Amplitude limiting field weakening filter | |||
| | |vlimmargin | ||
| - | |0 | ||
|10000 | |||
|2500 | |||
|Field weakening is brought in at modmax-vlimmargin. Increase if you get short bursts of unwanted regen at speed | |||
|fwcurmax | |||
|A | |||
| -1000 | |||
|0 | |0 | ||
| -100 | | -100 | ||
| | |Maximum field weakening current. Must be set to critical current of motor (TODO: link forum). Set to 0 for disabling field weakening | ||
|excurmax | |||
|A | |||
|0 | |||
|10 | |||
|0 | |||
|Exciter current maximum (Renault Zoe variant only) | |||
| | |lqminusld | ||
| | |mH | ||
| 0 | |||
|1000 | |||
| 0 | | 0 | ||
|Difference between d and q axis inductance. The higher, the more d-current is brought in for additional reluctance torque | |||
|fluxlinkage | |||
|mWeber | |||
|0 | |||
|1000 | |1000 | ||
| | |90 | ||
| | |Magnetic link between rotor and stator, shapes MTPA curve | ||
|syncadv | |syncadv | ||
|dig/Hz | |dig/Hz | ||
| | | 0 | ||
| | |65535 | ||
|10 | |10 | ||
|Shifts "syncofs" downwards/upwards with frequency | |Shifts "syncofs" downwards/upwards with frequency. Must be set so that ud remains at 0 when coasting below field weakening speed. '''SUPER DANGEROUS!''' Setting it wrong can cause unwanted acceleration. | ||
|''curkifrqgain'' | |||
|dig/Hz | |||
|0 | |||
|1000 | |||
|50 | |||
|Current controllers integral gain frequency coefficient (deprecated, removed) | |||
|''ffwstart'' | |||
|Hz | |||
|0 | |||
|1000 | |||
|200 | |||
|Starting point of field weakening controller. Below that frequency it is disabled, above it its gain is increased proportional to frequency and hits ''fwkp'' at ''fmax''. (deprecated, removed in latest release) | |||
| colspan="6" |'''Motor (sine)''' | | colspan="6" |'''Motor (sine)''' | ||
| Line 130: | Line 200: | ||
|400 | |400 | ||
|400 | |400 | ||
| | |Maximum slip is increased from fslipmax to fslipconstmax as frequency approaches this value. Only effective when greater than fweak. | ||
|udcnom | |udcnom | ||
| Line 158: | Line 228: | ||
|10 | |10 | ||
|5 | |5 | ||
|Slip frequency at maximum throttle and fconst | |Slip frequency at maximum throttle and fconst. Set equal to fslipmax to disable. | ||
|fmin | |fmin | ||
| Line 200: | Line 270: | ||
|0 | |0 | ||
| | |5 | ||
|0 | |0 | ||
|0=single channel encoder, 1=quadrature encoder, | |0=single channel encoder, 1=quadrature encoder, | ||
| Line 281: | Line 351: | ||
|Hardware over current limit. RMS-current times sqrt(2) + some slack. Set negative if il1gain and il2gain are negative. | |Hardware over current limit. RMS-current times sqrt(2) + some slack. Set negative if il1gain and il2gain are negative. | ||
|minpulse | |''minpulse'' | ||
|dig | |dig | ||
|0 | |0 | ||
|4095 | |4095 | ||
|1000 | |1000 | ||
|Narrowest or widest pulse, all other mapped to full off or full on, respectively | |Narrowest or widest pulse, all other mapped to full off or full on, respectively (Obsolete) | ||
|il1gain | |il1gain | ||
| Line 351: | Line 421: | ||
1xxx likewise with PWM 2 and 3 | 1xxx likewise with PWM 2 and 3 | ||
|modmax | |||
|dig | |||
|37000 | |||
|45000 | |||
|37836 | |||
|Values over 37836 over-modulate the PWM sine wave. This can achieve a slightly higher AC voltage at the expense of greater motor losses. (only "FOC" software) | |||
| colspan="6" |'''Derating''' | | colspan="6" |'''Derating''' | ||
| Line 402: | Line 479: | ||
| -5000 | | -5000 | ||
|Maximum DC output current (regen) | |Maximum DC output current (regen) | ||
|idckp | |||
|dig | |||
|0.1 | |||
|20 | |||
|2 | |||
|Proportional rate of DC current derating | |||
|idcflt | |||
|dig | |||
|0 | |||
|11 | |||
|9 | |||
|Filter co-efficient applied to idc prior to derating. Increasing this makes the DC current derating smoother. | |||
|tmphsmax | |||
|°C | |||
|50 | |||
|150 | |||
|85 | |||
|Maximum permitted temperature of the inverter heatsink. As the temperature gets within 10°C of this limit the throttle will be scaled back by 10% for every degree until it hits the limit. | |||
|tmpmmax | |||
|°C | |||
|70 | |||
|300 | |||
|300 | |||
|Maximum permitted temperature of the motor. As the temperature gets within 10°C of this limit the throttle will be scaled back by 10% for every degree until it hits the limit. | |||
|throtmax | |throtmax | ||
| Line 416: | Line 521: | ||
| -100 | | -100 | ||
|Throttle regen limit | |Throttle regen limit | ||
|accelmax | |||
|rpm/10ms | |||
|1 | |||
|1000 | |||
|1000 | |||
|Maximum permitted acceleration increase (traction control) | |||
|accelflt | |||
|dig | |||
|1 | |||
|5 | |||
|3 | |||
|Filter between the motor speed and the acceleration rate limiter. Higher values will smooth the input but will make the acceleration rate limiter react more slowly. | |||
|ifltrise | |ifltrise | ||
| Line 515: | Line 634: | ||
|0 | |0 | ||
| | |6 | ||
|0 | |0 | ||
|0=Pot 1 is throttle and pot 2 is regen strength preset | |0=Pot 1 is throttle and pot 2 is regen strength preset | ||
| Line 523: | Line 642: | ||
3=Throttle via CAN with redundancy (like 1) | 3=Throttle via CAN with redundancy (like 1) | ||
4=Bidirectional throttle sets torque and direction (e.g. for boats) | |||
6=Bidirectional throttle controlled via CAN (like 4) | |||
|potlinearity | |||
|0 | |||
|100 | |||
|100 | |||
|Blend between a fully linear pedal (100%) and fully quadratic (0%). The throttle output is defined as potnom²*(1-potlinearity) + potnom * potlinearity. Regen is always linear. | |||
|throtramp | |throtramp | ||
| Line 551: | Line 681: | ||
|50 | |50 | ||
|% positive throttle travel at which slip is increased (only "sine" software) | |% positive throttle travel at which slip is increased (only "sine" software) | ||
|sinecurve | |||
|0 | |||
|1 | |||
|0 | |||
|0=VoltageSlip - The first half of the throttle increases voltage but keeps slip at fslipin. Then the second half of the throttle increases slip up to fslipmax. | |||
1=Simultaneous - Increases slip and voltage at the same time across the whole range of the throttle. Can provide smoother throttle response. | |||
(only "sine" software) | |||
|throtfilter | |||
|dig | |||
|0 | |||
|10 | |||
|4 | |||
|How heavily the throttle is filtered. Lowering will increase throttle response at the expense of stability.(only "sine" software) | |||
|throtcur | |throtcur | ||
| Line 561: | Line 708: | ||
| colspan="6" |'''Regen''' | | colspan="6" |'''Regen''' | ||
|brknompedal | |brknompedal / brakeregen | ||
| -100 | | -100 | ||
| Line 573: | Line 720: | ||
|100 | |100 | ||
|100 | |100 | ||
|Ramp speed when entering regen. E.g. when you set brkmax to 30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% | |Ramp speed when entering regen. E.g. when you set brkmax to -30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% | ||
|brknom | |brknom / regentravel | ||
|0 | |0 | ||
| Line 582: | Line 729: | ||
|Range of throttle pedal travel allocated to regen | |Range of throttle pedal travel allocated to regen | ||
|brkmax | |brkmax / offthrotregen | ||
| | | -100 | ||
| | | 0 | ||
|30 | | -30 | ||
|Foot-off throttle regen torque | |Foot-off throttle regen torque | ||
|brkcruise | |brkcruise / cruiseregen | ||
| -100 | | -100 | ||
| Line 596: | Line 743: | ||
|Maximum regen of cruise control | |Maximum regen of cruise control | ||
|brkrampstr | |brkrampstr / regenrampstr | ||
|Hz | |Hz | ||
|0 | |0 | ||
| Line 603: | Line 750: | ||
|Below this frequency the regen torque is reduced linearly with the frequency | |Below this frequency the regen torque is reduced linearly with the frequency | ||
|brkout | |maxregentravelhz | ||
|Hz | |||
|0 | |||
|1000 | |||
|0 | |||
|Frequency at which full regentravel is used. Below this frequency regentravel is linearly scaled down with frequency. Allows deadzone-free throttle reaction at standstill and low speed | |||
|brkout / brklightout | |||
| -100 | | -100 | ||
| Line 631: | Line 785: | ||
|1 | |1 | ||
|0 | |0 | ||
|Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on | |Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on, 3=off, 4=Hill Hold | ||
|holdkp | |||
| -100 | |||
|0 | |||
| -0.25 | |||
|How hard the throttle should be applied to counteract rollback in hill hold. Higher values reduce rollback at the risk of introducing oscillation due to sensor noise. | |||
|speedkp | |speedkp | ||
| Line 653: | Line 814: | ||
|0 | |0 | ||
|0=button (set when button pressed, reset with brake pedal), 1=switch (set when switched on, reset when switched off or brake pedal) | |0=button (set when button pressed, reset with brake pedal), 1=switch (set when switched on, reset when switched off or brake pedal) | ||
|cruisethrotlim | |||
|0 | |||
|100 | |||
|50 | |||
|Amount of throttle cruise control is allowed to command | |||
| colspan="6" |'''Contactor Control''' | | colspan="6" |'''Contactor Control''' | ||
| Line 661: | Line 829: | ||
|1000 | |1000 | ||
|330 | |330 | ||
|Voltage at which the DC contactor is allowed to close | |Voltage at which the DC contactor is allowed to close. It appears that the pre-charge relay output goes low when power is applied to the Inverter. This setting causes the HV relay to go to ground once the inverter is started (in manual mode or via the start input) and the udc voltage climbs to the set value. If the udc voltage doesn't reach this value after 5 seconds, the inverter stops both relays by default and generates the Pre-Charge Fault. Setting this to 0 disables the pre-charge fault and skips the pre-charge state. Only set to 0 when manually doing pre-charge or when there is no high voltage connected inorder to test the outputs. | ||
Discussed around 37:00 minutes into the video linked above. | |||
|udcswbuck | |udcswbuck | ||
| Line 683: | Line 852: | ||
|0 | |0 | ||
|Engage precharge relay in boot loader. Introduced for enabling Prius Gen3 DC/DC converter when precharge relay is released. Use together with tripmode=2 | |Engage precharge relay in boot loader. Introduced for enabling Prius Gen3 DC/DC converter when precharge relay is released. Use together with tripmode=2 | ||
|outmode | |||
|0 | |||
|2 | |||
|0 | |||
|0=DC switch output, 1=Motor temp controls the fan output, 2=Heatsink temp controls fan output | |||
|fanthresh | |||
|°C | |||
|20 | |||
|300 | |||
|50 | |||
|Temperature at which the fan output is turned on when outmode is 1 or 2 | |||
| colspan="6" |'''Auxillary PWM''' | | colspan="6" |'''Auxillary PWM''' | ||
| Line 729: | Line 912: | ||
|1 | |1 | ||
|Node ID for CAN SDO messages and for selective enabling of UART when sharing one ESP8266 module between multiple processors. | |Node ID for CAN SDO messages and for selective enabling of UART when sharing one ESP8266 module between multiple processors. | ||
|controlid | |||
|1 | |||
|2047 | |||
|63 | |||
|The CAN ID used for controlling the [[CAN communication#Inverter_control_via_CAN_-_new!|controlling the inverter via CAN]] | |||
|controlcheck | |||
|0 | |||
|1 | |||
|1 | |||
|0=Check the counter field in canio CAN frames '''for legacy VCUs only''', 1=Validate the 8-bit truncated STM32 CRC in the canio frame | |||
| colspan="6" |'''Testing''' | | colspan="6" |'''Testing''' | ||
| Line 779: | Line 976: | ||
|uac | |uac | ||
|V | |V | ||
|Calculated AC voltage | |Calculated AC voltage (only "sine" software) | ||
|idc | |idc | ||
| Line 795: | Line 992: | ||
|il1rms | |il1rms | ||
|A | |A | ||
|RMS current L1 | |RMS current L1 (only "sine" software) | ||
|il2rms | |il2rms | ||
|A | |A | ||
|RMS current L2 | |RMS current L2 (only "sine" software) | ||
|ilmax | |ilmax | ||
|A | |A | ||
|Calculated max of il1, il2, il3 | |Calculated max of il1, il2, il3 (only "sine" software) | ||
|boostcalc | |boostcalc | ||
|A | |A | ||
|DC link adjusted boost setting | |DC link adjusted boost setting (only "sine" software) | ||
|fweakcalc | |fweakcalc | ||
|A | |A | ||
|DC link adjusted fweak setting | |DC link adjusted fweak setting (only "sine" software) | ||
|id | |||
|A | |||
|Current in the direct(d) axis (only "FOC" software) | |||
|iq | |||
|A | |||
|Current in the quadrature(q) axis (only "FOC" software) | |||
|ifw | |||
|A | |||
|Field weakening current (only "FOC" software) | |||
|ud | |||
|dig | |||
|Computed voltage in the direct(d) axis (only "FOC" software) | |||
|uq | |||
|dig | |||
|Computed voltage in the quadrature(q) axis (only "FOC" software) | |||
|uexc | |||
|dig | |||
|Computed exciter voltage (only "FOC" software for the Renault Zoe variant) | |||
|anticog | |||
|dig | |||
|Amplitude of the anti-cogging modulation waveform (only "FOC" software) | |||
|fstat | |fstat | ||
| Line 836: | Line 1,061: | ||
|Motor rotor angle, 0-360°. When using the SINE software, the slip is added to the rotor position. | |Motor rotor angle, 0-360°. When using the SINE software, the slip is added to the rotor position. | ||
This is not the physical angle, but a "virtual" angle. E.g. if your motor has four pole pairs (motor and resolver), then per one physical revolution the "angle" will change four times between 0 and 360°. Discussed here: https://openinverter.org/forum/viewtopic.php?p=71253#p71253 | |||
|pot | |pot | ||
| Line 844: | Line 1,070: | ||
|dig | |dig | ||
|Regen Pot value, 4095=max | |Regen Pot value, 4095=max | ||
|regenpreset | |||
|Regen preset value which can come from pot2 in potmode=0 or received via CAN | |||
|potnom | |potnom | ||
|Scaled pot value, 0 accel | |Scaled pot value, 0 accel. | ||
potnom also includes the deratings. So say you have programmed udcmin=300V and you are tuning without HV, so udc=0, potnom will never be positive because it thinks the battery voltage is low. Discussed here: https://openinverter.org/forum/viewtopic.php?p=62930#p62930 | |||
range: | |||
<nowiki>*</nowiki> negative means regeneration (e.g. -30%, according to [[Schematics and Instructions|Schematics and Instructions - openinverter.org wiki]]) | |||
<nowiki>*</nowiki> zero means "zero torque request" | |||
<nowiki>*</nowiki> 100% means full acceleraton. | |||
|dir / seldir | |||
|Selected rotation direction. -1=REV, 0=Neutral, 1=FWD | |||
| | |rotordir | ||
| | |Actual rotor direction | ||
|tmphs | |tmphs | ||
| Line 904: | Line 1,147: | ||
|Over current detected | |Over current detected | ||
|din_desat | |||
|Gate driver desaturation event | |||
|din_bms | |din_bms | ||
|BMS over voltage/under voltage | |BMS over voltage/under voltage | ||
|uptime | |||
|The number of 10ms ticks since power was applied to the inverter | |||
|cpuload | |cpuload | ||
| Line 940: | Line 1,191: | ||
When you feel satisfied with settings save them and go on setting regen and braking effect. | When you feel satisfied with settings save them and go on setting regen and braking effect. | ||
[[Category:OpenInverter]] [[Category:Inverter]] | |||
Latest revision as of 19:41, 14 March 2026
Motor Parameters
Example: boost=1700
Inverter Parameters
Parameter Reference
set param <value>
to change it. Type
get param
to get the current value.
| Motor (FOC) | |||||
| iqkp | 0 | 20000 | 64 | Current controller proportional gain. Low inductance/resistance motors need less, high inductance/resistance motors more | |
| idkp | 0 | 20000 | 64 | Same as above but often a little higher then iqkp | |
| curki | 0 | 100000 | 20000 | Current controller integral gain (id and iq) | |
| exckp | 0 | 20000 | 3000 | Exciter controller gain (Renault Zoe variant only) | |
| cogkp | -1000 | 1000 | 0 | Anti-cogging modulator gain. This generates a trapezoidal wave form to counter the cogging current of IPM motors. | |
| cogph | 0 | 65535 | 0 | Anti-cogging modulator phase angle between cogging current and electrical rotor angle | |
| cogmax | 0 | 30000 | 0 | Maximum amplitude of the anti-cogging current | |
| vlimflt | 0 | 16 | 10 | Amplitude limiting field weakening filter | |
| vlimmargin | 0 | 10000 | 2500 | Field weakening is brought in at modmax-vlimmargin. Increase if you get short bursts of unwanted regen at speed | |
| fwcurmax | A | -1000 | 0 | -100 | Maximum field weakening current. Must be set to critical current of motor (TODO: link forum). Set to 0 for disabling field weakening |
| excurmax | A | 0 | 10 | 0 | Exciter current maximum (Renault Zoe variant only) |
| lqminusld | mH | 0 | 1000 | 0 | Difference between d and q axis inductance. The higher, the more d-current is brought in for additional reluctance torque |
| fluxlinkage | mWeber | 0 | 1000 | 90 | Magnetic link between rotor and stator, shapes MTPA curve |
| syncadv | dig/Hz | 0 | 65535 | 10 | Shifts "syncofs" downwards/upwards with frequency. Must be set so that ud remains at 0 when coasting below field weakening speed. SUPER DANGEROUS! Setting it wrong can cause unwanted acceleration. |
| curkifrqgain | dig/Hz | 0 | 1000 | 50 | Current controllers integral gain frequency coefficient (deprecated, removed) |
| ffwstart | Hz | 0 | 1000 | 200 | Starting point of field weakening controller. Below that frequency it is disabled, above it its gain is increased proportional to frequency and hits fwkp at fmax. (deprecated, removed in latest release) |
| Motor (sine) | |||||
| boost | dig | 0 | 37813 | 1700 | 0 Hz Boost in digit. 1000 digit ~ 2.5% |
| fweakstrt | Hz | 0 | 1000 | 400 | Fweak value at potnom < 35%. Can improve low speed stability and reduce oscillation when set higher than fweak. Set equal to fweak to disable. |
| fweak | Hz | 0 | 400 | 67 | Frequency where V/Hz reaches its peak |
| fconst | Hz | 0 | 400 | 400 | Maximum slip is increased from fslipmax to fslipconstmax as frequency approaches this value. Only effective when greater than fweak. |
| udcnom | V | 0 | 1000 | 0 | Nominal voltage for fweak and boost. fweak and boost are scaled to the actual dc voltage. 0=don't scale |
| fslipmin | Hz | 0 | 100 | 1 | Slip frequency at minimum throttle |
| fslipmax | Hz | 0 | 100 | 3 | Slip frequency at maximum throttle |
| fslipconstmax | Hz | 0 | 10 | 5 | Slip frequency at maximum throttle and fconst. Set equal to fslipmax to disable. |
| fmin | Hz | 0 | 400 | 1 | Below this frequency no voltage is generated |
| Motor (common) | |||||
| polepairs | 1 | 16 | 2 | Pole pairs of motor (e.g. 4-pole motor: 2 pole pairs) | |
| respolepairs | 1 | 16 | 1 | Pole pairs of resolver (normally same as polepairs of motor, but sometimes 1) | |
| sincosofs | dig | 0 | 4096 | 2048 | Mid point of sin/cos chip |
| encflt | 0 | 16 | 4 | Filter constant between pulse encoder and speed calculation. Makes up for slightly uneven pulse distribution | |
| encmode | 0 | 5 | 0 | 0=single channel encoder, 1=quadrature encoder,
| fmax | Hz | 0 | 400 | 200 | At this frequency rev limiting kicks in |
| numimp | Imp/rev | 8 | 8192 | 60 | Pulse encoder pulses per turn |
| dirchrpm | rpm | 0 | 2000 | 100 | Motor speed at which direction change is allowed |
| dirmode | 0 | 1 | 1 | 0=button (momentary pulse selects forward/reverse), 1=switch (forward or reverse signal must be constantly high) | |
| syncofs | dig | 0 | 65535 | 0 | Phase shift of sine wave after receiving index pulse |
| snsm | 2 | 3 | 2 | Motor temperature sensor. 12=KTY83, 13=KTY84, 14=Leaf, 15=KTY81 | |
| Inverter | |||||
| pwmfrq | 0 | 3 | 2 | PWM frequency. 0=17.6kHz, 1=8.8kHz, 2=4.4kHz, 3=2.2kHz. Needs PWM restart | |
| pwmpol | 0 | 1 | 0 | PWM polarity. 0=active high, 1=active low. DO NOT PLAY WITH THIS!
| deadtime | dig | 0 | 255 | 28 | Deadtime between highside and lowside pulse. 28=800ns, 56=1.5µs. Not always linear, consult STM32 manual. Needs PWM restart |
| ocurlim | A | -65535 | 65535 | 100 | Hardware over current limit. RMS-current times sqrt(2) + some slack. Set negative if il1gain and il2gain are negative. |
| minpulse | dig | 0 | 4095 | 1000 | Narrowest or widest pulse, all other mapped to full off or full on, respectively (Obsolete) |
| il1gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L1 |
| il2gain | dig/A | 0 | 4095 | 4.7 | Digits per A of current sensor L2 |
| udcgain | dig/V | 0 | 4095 | 6.15 | Digits per V of DC link |
| udcofs | dig | 0 | 4095 | 0 | DC link 0V offset |
| udclim | V | 0 | 1000 | 540 | High voltage at which the PWM is shut down |
| snshs | 0 | 1 | 0 | Heatsink temperature sensor. 0=JCurve, 1=Semikron, 2=MBB600, 3=KTY81, 4=PT1000, 5=NTCK45+2k2, 6=Leaf | |
| pinswap | 0 | 7 | 0 | Swap pins (only "FOC" software). Multiple bits can be set. 1=Swap Current Inputs, 2=Swap Resolver sin/cos, 4=Swap PWM output 1/3
0001 = 1 Swap Currents ony 0010 = 2 Swap Resolver only 0011 = 3 Swap Resolver and Currents 0100 = 4 Swap PWM 1 and 3 only 0101 = 5 Swap PWM 1 and 3 and Currents 0110 = 6 Swap PWM 1 and 3 and Resolver 0111 = 7 Swap PWM 1 and 3 and Resolver and Currents 1xxx likewise with PWM 2 and 3 | |
| modmax | dig | 37000 | 45000 | 37836 | Values over 37836 over-modulate the PWM sine wave. This can achieve a slightly higher AC voltage at the expense of greater motor losses. (only "FOC" software) |
| Derating | |||||
| bmslimhigh | % | 0 | 100 | 50 | Positive throttle limit on BMS under voltage |
| bmslimlow | % | -100 | 0 | -1 | Regen limit on BMS over voltage |
| udcmin | V | 0 | 1000 | 450 | Minimum battery voltage |
| udcmax | V | 0 | 1000 | 520 | Maximum battery voltage |
| iacmax | A | 0 | 5000 | 5000 | Maximum peak AC current |
| idcmax | A | 0 | 5000 | 5000 | Maximum DC input current |
| idcmin | A | -5000 | 0 | -5000 | Maximum DC output current (regen) |
| idckp | dig | 0.1 | 20 | 2 | Proportional rate of DC current derating |
| idcflt | dig | 0 | 11 | 9 | Filter co-efficient applied to idc prior to derating. Increasing this makes the DC current derating smoother. |
| tmphsmax | °C | 50 | 150 | 85 | Maximum permitted temperature of the inverter heatsink. As the temperature gets within 10°C of this limit the throttle will be scaled back by 10% for every degree until it hits the limit. |
| tmpmmax | °C | 70 | 300 | 300 | Maximum permitted temperature of the motor. As the temperature gets within 10°C of this limit the throttle will be scaled back by 10% for every degree until it hits the limit. |
| throtmax | % | 0 | 100 | 100 | Throttle limit |
| throtmin | % | -100 | 0 | -100 | Throttle regen limit |
| accelmax | rpm/10ms | 1 | 1000 | 1000 | Maximum permitted acceleration increase (traction control) |
| accelflt | dig | 1 | 5 | 3 | Filter between the motor speed and the acceleration rate limiter. Higher values will smooth the input but will make the acceleration rate limiter react more slowly. |
| ifltrise | dig | 0 | 32 | 10 | Controls how quickly slip and amplitude recover. The greater the value, the slower |
| ifltfall | dig | 0 | 32 | 3 | Controls how quickly slip and amplitude are reduced on over current. The greater the value, the slower |
| Charger | |||||
| chargemode | 0 | 4 | 0 | 0=Off, 3=Boost, 4=Buck | |
| chargecur | 0 | 50 | 0 | Charge current setpoint. Boost mode: charger INPUT current. Buck mode: charger output current | |
| chargekp | 0 | 100 | 80 | Charge controller proportional gain. Lower if you have oscillation, raise to get best power factor. | |
| chargeki | 0 | 100 | 10 | Charge controller integral gain. | |
| chargeflt | 0 | 10 | 8 | Charge current filtering. Raise if you have oscillations | |
| chargepwmin | % | 0 | 99 | 0 | Lowest charge mode duty cycle. This is needed for synchronous converters like in the Prius Gen2 where the lower IGBT is also active in buck mode and actually boosts the battery voltage into the bus capacitor when duty cycle is low. |
| chargepwmax | % | 0 | 99 | 90 | Charge mode duty cycle limit. Especially in boost mode this makes sure you don't overvolt you IGBTs if there is no battery connected. |
| Throttle | |||||
| potmin | dig | 0 | 4095 | 0 | Value of "pot" when pot isn't pressed at all |
| potmax | dig | 0 | 4095 | 4095 | Value of "pot" when pot is pushed all the way in |
| pot2min | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in 0 position |
| pot2max | dig | 0 | 4095 | 4095 | Value of "pot2" when regen pot is in full on position |
| potmode | 0 | 6 | 0 | 0=Pot 1 is throttle and pot 2 is regen strength preset
1=Pot 2 is proportional to pot 1 (redundancy) 2=Throttle/regen controlled via CAN (like 0) 3=Throttle via CAN with redundancy (like 1) 4=Bidirectional throttle sets torque and direction (e.g. for boats) 6=Bidirectional throttle controlled via CAN (like 4) | |
| potlinearity | % | 0 | 100 | 100 | Blend between a fully linear pedal (100%) and fully quadratic (0%). The throttle output is defined as potnom²*(1-potlinearity) + potnom * potlinearity. Regen is always linear. |
| throtramp | %/10ms | 0 | 100 | 100 | Max positive throttle slew rate |
| throtramprpm | rpm | 0 | 20000 | 20000 | No throttle ramping above this speed |
| ampmin | % | 0 | 100 | 10 | Minimum relative sine amplitude (only "sine" software) |
| slipstart | % | 10 | 100 | 50 | % positive throttle travel at which slip is increased (only "sine" software) |
| sinecurve | 0 | 1 | 0 | 0=VoltageSlip - The first half of the throttle increases voltage but keeps slip at fslipin. Then the second half of the throttle increases slip up to fslipmax.
1=Simultaneous - Increases slip and voltage at the same time across the whole range of the throttle. Can provide smoother throttle response. (only "sine" software) | |
| throtfilter | dig | 0 | 10 | 4 | How heavily the throttle is filtered. Lowering will increase throttle response at the expense of stability.(only "sine" software) |
| throtcur | A/% | -10 | 10 | 1 | Motor current per % of throttle travel (only "FOC" software) |
| Regen | |||||
| brknompedal / brakeregen | % | -100 | 0 | -50 | Foot on brake pedal regen torque |
| regenramp | %/10ms | 0.1 | 100 | 100 | Ramp speed when entering regen. E.g. when you set brkmax to -30% and regenramp to 1, it will take 300ms to arrive at brake force of -60% |
| brknom / regentravel | % | 0 | 100 | 30 | Range of throttle pedal travel allocated to regen |
| brkmax / offthrotregen | % | -100 | 0 | -30 | Foot-off throttle regen torque |
| brkcruise / cruiseregen | % | -100 | 0 | -30 | Maximum regen of cruise control |
| brkrampstr / regenrampstr | Hz | 0 | 400 | 10 | Below this frequency the regen torque is reduced linearly with the frequency |
| maxregentravelhz | Hz | 0 | 1000 | 0 | Frequency at which full regentravel is used. Below this frequency regentravel is linearly scaled down with frequency. Allows deadzone-free throttle reaction at standstill and low speed |
| brkout / brklightout | % | -100 | -1 | -50 | Activate brake light output at this amount of braking force |
| Automation | |||||
| idlespeed | rpm | -100 | 1000 | -100 | Motor idle speed. Set to -100 to disable idle function. When idle speed controller is enabled, brake pedal must be pressed on start. |
| idlethrotlim | % | 0 | 100 | 50 | Throttle limit of idle speed controller |
| idlemode | 0 | 1 | 0 | Motor idle speed mode. 0=always run idle speed controller, 1=only run it when brake pedal is released, 2=like 1 but only when cruise switch is on, 3=off, 4=Hill Hold | |
| holdkp | -100 | 0 | -0.25 | How hard the throttle should be applied to counteract rollback in hill hold. Higher values reduce rollback at the risk of introducing oscillation due to sensor noise. | |
| speedkp | Hz | 0 | 100 | 1 | Speed controller gain (Cruise and idle speed). Decrease if speed oscillates. Increase for faster load regulation |
| speedflt | dig | 0 | 16 | 1 | Filter before cruise controller |
| cruisemode | 0 | 1 | 0 | 0=button (set when button pressed, reset with brake pedal), 1=switch (set when switched on, reset when switched off or brake pedal) | |
| cruisethrotlim | % | 0 | 100 | 50 | Amount of throttle cruise control is allowed to command |
| Contactor Control | |||||
| udcsw | V | 0 | 1000 | 330 | Voltage at which the DC contactor is allowed to close. It appears that the pre-charge relay output goes low when power is applied to the Inverter. This setting causes the HV relay to go to ground once the inverter is started (in manual mode or via the start input) and the udc voltage climbs to the set value. If the udc voltage doesn't reach this value after 5 seconds, the inverter stops both relays by default and generates the Pre-Charge Fault. Setting this to 0 disables the pre-charge fault and skips the pre-charge state. Only set to 0 when manually doing pre-charge or when there is no high voltage connected inorder to test the outputs.
| udcswbuck | V | 0 | 1000 | 540 | Voltage at which the DC contactor is allowed to close in buck charge mode |
| tripmode | 0 | 2 | 0 | What to do with relays at a shutdown event. 0=All off, 1=Keep DC switch closed, 2=close precharge relay | |
| bootprec | 0 | 1 | 0 | Engage precharge relay in boot loader. Introduced for enabling Prius Gen3 DC/DC converter when precharge relay is released. Use together with tripmode=2 | |
| outmode | 0 | 2 | 0 | 0=DC switch output, 1=Motor temp controls the fan output, 2=Heatsink temp controls fan output | |
| fanthresh | °C | 20 | 300 | 50 | Temperature at which the fan output is turned on when outmode is 1 or 2 |
| Auxillary PWM | |||||
| pwmfunc | 0 | 2 | 0 | Quantity that controls the PWM output. 0=tmpm, 1=tmphs, 2=speed | |
| pwmgain | dig/C | 0 | 65535 | 100 | Gain of PWM output |
| pwmofs | dig | -65535 | 65535 | 0 | Offset of PWM output, 4096=full on |
| Communication | |||||
| canspeed | 0 | 3 | 0 | Baud rate of CAN interface 0=250k, 1=500k, 2=800k, 3=1M | |
| canperiod | 0 | 1 | 0 | 0=send configured CAN messages every 100ms, 1=every 10ms | |
| nodeid | 1 | 63 | 1 | Node ID for CAN SDO messages and for selective enabling of UART when sharing one ESP8266 module between multiple processors. | |
| controlid | 1 | 2047 | 63 | The CAN ID used for controlling the controlling the inverter via CAN | |
| controlcheck | 0 | 1 | 1 | 0=Check the counter field in canio CAN frames for legacy VCUs only, 1=Validate the 8-bit truncated STM32 CRC in the canio frame | |
| Testing | |||||
| fslipspnt | Hz | -100 | 100 | 0 | Slip setpoint in mode 2. Written by software in mode 1 |
| ampnom | % | 0 | 100 | 0 | Nominal amplitude in mode 2. Written by software in mode 1 |
Spot values
get
get il1,il2,udc
| Name | Unit | Description |
| version | Firmware version | |
| hwver | Hardware version | |
| opmode | Operating mode. 0=Off, 1=Run, 2=Manual_run, 3=Boost, 4=Buck, 5=Sine, 6=2 Phase sine | |
| lasterr | Last error message | |
| udc | V | DC link voltage |
| uac | V | Calculated AC voltage (only "sine" software) |
| idc | A | Calculated DC current |
| il1 | A | AC current L1 |
| il2 | A | AC current L2 |
| il1rms | A | RMS current L1 (only "sine" software) |
| il2rms | A | RMS current L2 (only "sine" software) |
| ilmax | A | Calculated max of il1, il2, il3 (only "sine" software) |
| boostcalc | A | DC link adjusted boost setting (only "sine" software) |
| fweakcalc | A | DC link adjusted fweak setting (only "sine" software) |
| id | A | Current in the direct(d) axis (only "FOC" software) |
| iq | A | Current in the quadrature(q) axis (only "FOC" software) |
| ifw | A | Field weakening current (only "FOC" software) |
| ud | dig | Computed voltage in the direct(d) axis (only "FOC" software) |
| uq | dig | Computed voltage in the quadrature(q) axis (only "FOC" software) |
| uexc | dig | Computed exciter voltage (only "FOC" software for the Renault Zoe variant) |
| anticog | dig | Amplitude of the anti-cogging modulation waveform (only "FOC" software) |
| fstat | Hz | Stator frequency |
| speed | rpm | Motor speed |
| cruisespeed | rpm | Motor RPM set point for cruise control if cruisemode=CAN |
| turns | Number of turns the motor completed since power up | |
| amp | dig | Sine amplitude, 37813=max |
| angle | ° | Motor rotor angle, 0-360°. When using the SINE software, the slip is added to the rotor position.
| pot | dig | Pot value, 4095=max |
| pot2 | dig | Regen Pot value, 4095=max |
| regenpreset | % | Regen preset value which can come from pot2 in potmode=0 or received via CAN |
| potnom | % | Scaled pot value, 0 accel.
potnom also includes the deratings. So say you have programmed udcmin=300V and you are tuning without HV, so udc=0, potnom will never be positive because it thinks the battery voltage is low. Discussed here: https://openinverter.org/forum/viewtopic.php?p=62930#p62930 range: * negative means regeneration (e.g. -30%, according to Schematics and Instructions - openinverter.org wiki) * zero means "zero torque request" * 100% means full acceleraton. |
| dir / seldir | Selected rotation direction. -1=REV, 0=Neutral, 1=FWD | |
| rotordir | Actual rotor direction | |
| tmphs | °C | Heatsink temperature |
| tmpm | °C | Motor temperature |
| uaux | V | Auxiliary voltage (i.e. 12V system). Measured on pin 11 (mprot) |
| pwmio | raw state of PWM outputs at power up | |
| canio | Digital IO bits received via CAN | |
| din_cruise | Cruise Control. This pin activates the cruise control with the current speed. Pressing again updates the speed set point. | |
| din_start | State of digital input "start". This pin starts inverter operation | |
| din_brake | State of digital input "brake". This pin sets maximum regen torque (brknompedal). Cruise control is disabled. | |
| din_mprot | State of digital input "motor protection switch". Shuts down the inverter when =0 | |
| din_forward | Direction forward | |
| din_reverse | Direction backward | |
| din_emcystop | State of digital input "emergency stop". Shuts down the inverter when =0 | |
| din_ocur | Over current detected | |
| din_desat | Gate driver desaturation event | |
| din_bms | BMS over voltage/under voltage | |
| uptime | The number of 10ms ticks since power was applied to the inverter | |
| cpuload | % | CPU load for everything except communication |
Tuning Guide